Appropriate Septic tank Cleaning (emptying) Frequency

46.4k views

Page selection:
  • aasimmansuri
  • aasimmansuri's Avatar
    Topic Author
  • Engineer Planner, Senior Program Lead at Center for Water and Sanitation, CEPT University
  • Posts: 36
  • Karma: 1
  • Likes received: 10

Re: Appropriate Septic tank Cleaning (emptying) Frequency

Hi Elisabeth,

Agree to most of the points highlighted by Mr. Pawan.

In India it is still not mandated to clean septic tanks at an interval of 2-3 years as prescribed by the CPHEEO manual. Also the septic tanks here have large cleaning frequency because of over sized septic tanks.

But here we do have General development control regulations (GDCR) and National building code that all cities have to follow. But this regulations only give an outline on how the septic tank should be designed for eg. length to breath ratio has to be 2:4, but this does not give a definite size of septic tank as per the user size and cleaning frequency as mentioned in the CPHEEO manual, 2013

Also in 2013, we had an advisory on septage management from Govt. of India which now prescribes that septic tanks need to be cleaned at an interval of 2-3 years and with new national programmes like AMRUT which lays emphasis on septage management, we are optimistic that this prescribed norms may just be mandated.

In the cities that we are working in Maharashtra we are developing this scheduled fecal sludge emptying plan and the city government is on-board with us with 3 year of emptying cycle and we are planning to finance this plan through introduction of a special sanitary tax on annual basis which comes out to be less than what the people are presently paying for getting their septic tanks emptied.

Also, there was a World Bank project in 100 rural villages of Punjab, where they had implemented settled sewer in these villages and it was mandated that households had to clean their septic tanks once in 2 years.

Regards,
Aasim
Aasim Mansuri
Senior Program Lead
Center for Water and Sanitation
CEPT University, Ahmedabad-380009, Gujarat, India
M: +91 98 98 324874 | O: +91 79 26302470

This email address is being protected from spambots. You need JavaScript enabled to view it. l This email address is being protected from spambots. You need JavaScript enabled to view it. | www.pas.org.in
fb.com/pas.cept | linkedin.com/in/pascept

Please Log in to join the conversation.

You need to login to reply
  • pkjha
  • pkjha's Avatar
  • Working for over 30 years in the fields of sanitation, biogas from human wastes, septage management, waste water treatment in rural as well as urban areas in India and other developing countries.
  • Posts: 178
  • Karma: 11
  • Likes received: 74

Re: Appropriate Septic tank Cleaning (emptying) Frequency

Dear Elisabeth

In India there is one Manual on Sewerage and Sewage Treatment, from CPHEEO, Ministry of Urban Development, Government of India. Its latest edition is of 2013. Chapter 9 of the Manual deals with on-site sanitation including Septic Tanks.
Size of septic tank and its emptying intervals is perhaps never followed as per the Manual, neither is it a mandate. In fact septic tanks are constructed by masons who never know the Manual and CPHEEO. Size of a septic tank is decided by the concerned masons and households depending on their affordability /economic status. Larger size of tank is considered better as its emptying interval is longer.
Emptying is carried out only when the tanks are completely filled and there is physically blockage of sewage from toilet Pan to tanks. Depending on the size of tanks, cleaning interval varies between 5-10 years or even more. At initial years there is treatment of sewage with better effluent quality due to longer retention time, but in subsequent years there is practically no treatment after the tanks are filled. Practically such septic tanks act as storage tanks.
Status of septic tanks linked with public/ community toilets is worse. In most of the cases, such tanks are of undersized, due to lack of space or fund or both. In this case also emptying is done only after there is back flow of sewage. Most of such toilets are maintained on pay and use basis by service providers/ contractors. They are rarely concerned with the treatment of sewage; they are more concerned with economic aspects. To follow the Manual to emptying the tanks ( in 1-2 years) will cost more and hence not interested.
Regards

Pawan
Pawan Jha
Chairman
Foundation for Environment and Sanitation
Mahavir Enclave
New Delhi 110045, India
Web: www.foundation4es.org
Linked: linkedin.com/in/drpkjha
The following user(s) like this post: Elisabeth

Please Log in to join the conversation.

You need to login to reply
  • Elisabeth
  • Elisabeth's Avatar
  • Moderator
  • Freelance consultant since 2012 (former roles: program manager at GIZ and SuSanA secretariat, lecturer, process engineer for wastewater treatment plants)
  • Posts: 3372
  • Karma: 54
  • Likes received: 931

Re: Appropriate Septic tank Cleaning (emptying) Frequency

Dear Aasim,

I just wanted to go back to what you said at the beginning of this thread three years ago:

In India there are codes and manuals which have standardized size and cleaning frequency of septic tank.These suggest a maximum interval of 2 years for cleaning of septic tanks and related sizes linked to loads.


Do these codes actually mandate that the septic tank is emptied every two years (I would call it "emptying", not "cleaning"), or is it more like a general recommendation?

In your work with faecal sludge management systems in the last few years as part of your PAS (Performance assessment system) project (see here on the forum: forum.susana.org/forum/categories/183-mo...niversity-india#9784), have you come across any cities in India that are doing scheduled septic tank emptying programmes?

This is something that we recently discussed here on the forum under the theme of city-level financing and full cost recovery of urban sanitation:
forum.susana.org/forum/categories/192-th...ire-sanitation-chain

You, or anyone following this thread, might like to take a look at that new thread and react to some of the points raised there. Thanks.

By the way, faecal sludge transfer stations were also mentioned in this thread a year ago, and are now being discussed in another structured discussion here on the forum:
forum.susana.org/forum/categories/99-fae...ge-transfer-stations

Regards,
Elisabeth
Dr. Elisabeth von Muench
Freelance consultant on environmental and climate projects
Located in Ulm, Germany
This email address is being protected from spambots. You need JavaScript enabled to view it.
My Wikipedia user profile: en.wikipedia.org/wiki/User:EMsmile
LinkedIn: www.linkedin.com/in/elisabethvonmuench/

Please Log in to join the conversation.

You need to login to reply
  • Florian
  • Florian's Avatar
  • Water and Sanitation Specialist at Skat Consulting Ltd.
  • Posts: 269
  • Karma: 22
  • Likes received: 131

Re: septage management in Haiphong

jonpar wrote: Florian - can you give more information about septage management in Haiphong. I am particularly interested in the mobile transfer stations and the "free" septic tank cleaning service every 5 years (with costs being covered by the waste water tariff). Looking forward to hearing more about this. best regards, Jonathan


Hi Jonathan,
sorry for being late, I missed your post as I was away for a while (incidently in Vietnam, but for holidays this time, not checking on septic tanks ;) )

My own experience with Hai Phong is a bit outdated and limited. In 2001 I did a 1 day visit there. It is documented briefly in this document: www.eawag.ch/forschung/sandec/publikatio...m/dl/FSM_Vietnam.pdf

Here a copy of the respective paragraph:
"Haiphong (pop. 400,000)
The Sewer and Drainage Company is responsible for septage collection. Collection is car-
ried out with vacuum tankers and small vacuum tugs for areas difficult to access, used together with intermediate-storage-tanks mounted on a hook-lift truck. The mini-vacuum-tugs were developed by the company in collaboration with a local manufacturer. They have a capacity of 350 L and cost around 4000 $. The combination of large and small equipment has proven successful and almost 100% of the houses can be covered. The septage is disposed on the landfill, which is not perceived as satisfactory solution by the Finnish Water Supply and Sanitation Project. A future World Bank project will contain a component for septage treatment, drying beds were mentioned as possible treatment option"

The "Landscape Analysis and Business Model Assessment in Fecal Sludge Management: Extraction and Transportation Models in Vietnam - Final report" financed by BMGF and done by the Hanoi University of Civil Engineering has a detailed description of sludge management in Hai Phong, probably answering most of your questions. If you need more info, you'll need to ask the author, Prof. Nguyet Viet Anh. He's the one to ask for anything sludge or sanitation in Vietnam.

Other institutions to ask would be the GIZ programme on wastewater GIZ programme on wastewater (they have done quite some work on decentralised urban sanitation and septic tanks in northern Vietnam) or Sandec (they currently have a PhD student working on fecal sludge in Vietnam, perhaps they have more recent info on Hai Phong).

Best wishes, Florian

Please Log in to join the conversation.

You need to login to reply
  • vdamato
  • vdamato's Avatar
  • Posts: 2
  • Likes received: 0

Re: Appropriate Septic tank Cleaning Frequency

Hey all -

Check out this guidance document on septic tank performance that I did for the Water Environment Research Foundation a few years back: Factors Affecting the Performance of Primary Treatment in Decentralized Wastewater Systems . The Research Digest is the most detailed product. See pages 2 and 17, in particular.

Your observation of longer desludging intervals for relatively larger tanks is supported by published research. Theoretically, the longer sludge age should better facilitate methanogenesis and likewise, more complete treatment of organic cabon. Additionally, as has been stated, the rate of sludge accumulation will be lower since you will have more efficient digestion of the settled sludge. I personally support "oversizing" (relative to rule-of-thumb standards) septic tanks. I don't see any particular drawback and several potential benefits, although those benefits are not fully documented in the literature.

Vic
Victor D'Amato, PE
Senior Engineer, Sustainable Design
PO Box 14409
Research Triangle Park, NC, USA. 27312
919.485.2070
This email address is being protected from spambots. You need JavaScript enabled to view it.

Please Log in to join the conversation.

You need to login to reply
  • pkjha
  • pkjha's Avatar
  • Working for over 30 years in the fields of sanitation, biogas from human wastes, septage management, waste water treatment in rural as well as urban areas in India and other developing countries.
  • Posts: 178
  • Karma: 11
  • Likes received: 74

Re: Appropriate Septic tank Cleaning Frequency

Dear Aasim

In an over sized septic tank -cleaned after 5-10 years, sludge at bottom of the tank becomes more compact. In such case tank can't be emptied through sludge pump.It requires manual labour to clean the bottom of the tank. In some cases such sludge is disintegrated applying forced water. It is a cumbersome process and there is unnecessary loss of water.Cost of such septic tank is obviously quite high. It discourages other people of the community to adopt this technology. In case of over size tanks, quality of effluent- in term of BOD, COD, suspended solids would be better in early months due to high retention time of the tank. However, at later stage -when the tanks are filled, quality of effluent would decrease considerably.
regards
Pawan
Pawan Jha
Chairman
Foundation for Environment and Sanitation
Mahavir Enclave
New Delhi 110045, India
Web: www.foundation4es.org
Linked: linkedin.com/in/drpkjha

Please Log in to join the conversation.

You need to login to reply
  • aasimmansuri
  • aasimmansuri's Avatar
    Topic Author
  • Engineer Planner, Senior Program Lead at Center for Water and Sanitation, CEPT University
  • Posts: 36
  • Karma: 1
  • Likes received: 10

Re: Appropriate Septic tank Cleaning Frequency

Hi Jonathan,

Following is a link to the page from where you may find more details on the Haiphong septage Management.

www.waterlinks.org/partnerships/iwk-haiphong-septage-management

Hope its useful.

Regards,
Aasim
Aasim Mansuri
Senior Program Lead
Center for Water and Sanitation
CEPT University, Ahmedabad-380009, Gujarat, India
M: +91 98 98 324874 | O: +91 79 26302470

This email address is being protected from spambots. You need JavaScript enabled to view it. l This email address is being protected from spambots. You need JavaScript enabled to view it. | www.pas.org.in
fb.com/pas.cept | linkedin.com/in/pascept

Please Log in to join the conversation.

You need to login to reply
  • jonpar
  • jonpar's Avatar
  • As part of the Engineering team, my role at IMC is to lead on the delivery of projects requiring specific expertise on urban sanitation (including excreta/waste/wastewater/stormwater management) focusing on technical, institutional and financial aspects in project design and implementation.
  • Posts: 223
  • Karma: 24
  • Likes received: 87

Re: Appropriate Septic tank Cleaning Frequency

many thanks Cecile. I didn't know they had the same arrangement in Manila. Can anyone provide me with more information about the transfer stations referred to in Florian's email ? best regards, Jonathan
Dr. Jonathan Parkinson
Principal Consultant – Water and Sanitation
IMC Worldwide Ltd, Redhill, United Kingdom
Email: This email address is being protected from spambots. You need JavaScript enabled to view it.
Skype : jonathanparkinson1

Please Log in to join the conversation.

You need to login to reply
  • cecile
  • cecile's Avatar
  • Moderator
  • Water and Sanitation Sector Leader for SNV in Burkina Faso
  • Posts: 197
  • Karma: 13
  • Likes received: 80

Re: Appropriate Septic tank Cleaning Frequency

christoph wrote: Hello,
situations where no grey water goes to the septic tank help a lot (just practical observation by operating a fecal sludge truck, no scientific investigation)


@ Christoph : what could be the reason for this, Christoph ?
I would tend to think that on the contrary, if there is no grey water in the septic tank then the fluid inside the septic tank would be quite viscous and too thick to pump out. I have heard (but I haven't seen in directly) that in that case the desludging operators have to introduce (pressurised) water to facilitate the suction.

@Jonpar : the same system exists in Manila in the Philippines. I attached an extract of research and presentation (dates back to 2008)

Some time ago we had a discussion on the forum (forum.susana.org/forum/categories/53-fae...em?limit=12&start=12)about Effective Microorganisms in the form of additives / powders sold on the market and their efficiency on decreasing sludge formation at the bottom of the tanks and therefore spacing the clearing frequency. I talked about this with a decentralised sanitation technician who said he observed a very good effectiveness of the Eparcyl additive : one mechanical action because the powder is made of small solids, sort of small balls which are suspended in the liquid area of the sludge (media to fix bacteria) and contains biological agents which enhance the bacterial activity (yogourt type bacteria). Without being a magical treatment it seems that it does have a positive impact on the clearing frequency.

Cheers,

Cecile
Cécile Laborderie
MAKATI Environnement

This message has an attachment file.
Please log in or register to see it.

Please Log in to join the conversation.

You need to login to reply
  • jonpar
  • jonpar's Avatar
  • As part of the Engineering team, my role at IMC is to lead on the delivery of projects requiring specific expertise on urban sanitation (including excreta/waste/wastewater/stormwater management) focusing on technical, institutional and financial aspects in project design and implementation.
  • Posts: 223
  • Karma: 24
  • Likes received: 87

Re: septage management in Haiphong

Florian - can you give more information about septage management in Haiphong. I am particularly interested in the mobile transfer stations and the "free" septic tank cleaning service every 5 years (with costs being covered by the waste water tariff). Looking forward to hearing more about this. best regards, Jonathan
Dr. Jonathan Parkinson
Principal Consultant – Water and Sanitation
IMC Worldwide Ltd, Redhill, United Kingdom
Email: This email address is being protected from spambots. You need JavaScript enabled to view it.
Skype : jonathanparkinson1

Please Log in to join the conversation.

You need to login to reply
  • mwaniki
  • mwaniki's Avatar
  • Posts: 145
  • Karma: 4
  • Likes received: 22

Re: Septic tank diagram

Dear All

Could someone kindly remind me where I could find a simple septic tank diagram accompanied by notes for construction by a semi-urban community possibly with a consideration of a good suction system to flush out the faecal sludge.

Kind regards

S.Mwaniki
Publisher - Africa Water, Sanitation & Hygiene
Am the publisher of the Africa Water,Sanitation & Hygiene and the C.E.O. of Transworld Publishers Ltd.,Nairobi-Kenya.

Please Log in to join the conversation.

You need to login to reply
  • Marijn Zandee
  • Marijn Zandee's Avatar
  • Moderator
  • No longer working in WASH, but still following the forum.
  • Posts: 261
  • Karma: 22
  • Likes received: 134

Re: Appropriate Septic tank Cleaning Frequency

Dear Aasim,

To the best of my understanding, the fact that the septic tank is bigger then prescribed in codes should not stop it from functioning.

If you measure very high BOD in the effluent the following comes to mind:

1.) Despite the tank being larger than the codes, the level of solids has actually reached the point where the retention time is too small. (Tank is full).

2.) People use very aggressive cleaning agents, which affect the bacterial processes.

Have you opened any of the tanks that have high BOD effluent? If not, that would be a good first step to check if there is a scum (foam) layer indicating a working process and to check solid levels.

If you have opened some tanks already, please share your findings.

Kind regards

Marijn
Marijn Zandee

E: This email address is being protected from spambots. You need JavaScript enabled to view it.

Please Log in to join the conversation.

You need to login to reply
Page selection:
Share this thread:
Recently active users. Who else has been active?
Time to create page: 0.086 seconds
Powered by Kunena Forum